On Wed, 17 Sep 2008 08:03:36 -0700 (PDT) w_tom <***@usa.net> wrote:
| On Sep 16, 11:31 pm, phil-news-***@ipal.net wrote:
|>> Either way, the 'whole house' protector is for all types of surges.
|>
|> Why do you think this is so?
|> It is NOT so. No ONE protector completely eliminates any surge.
|> The whole house protector connected at the entrance point and grounded
|> does NOT divert all energy to ground. It only diverts part of it to
|> ground. The only way it could divert all energy to ground is to have
|> NO OTHER CONNECTION except ground (and the source of energy).
|
| The 'whole house' protector is so sufficient that most all surge
| energy goes to ground (dissipated harmlessly) via a low impedance
| path. Any surge that would seek earth ground via those long romex
| wires is so trivial as to be made irrelevant by protection inside all
| appliances.
You have a pair of wires that reaches a junction. That junction has
two additional pairs of wires. There are a total of 3 pairs of wires
at this junction. We can label them A, B, and C.
A surge propogating over wire pair A reaches the junctions. The surge
somehow "knows" that wire pair B is attached to ground and wire pair C
is not attached to ground. The surge "chooses" to travel over wire
pair B and not wire pair C.
Do you actually believe the above scenario really happens?
| But again, the numbers. Assume a plug-in protector will earth a
| trivial 100 amp surge via 50 feet of inside the wall (romex) wire.
| Wire impedance says that voltage from appliance to breaker box is
| something less than 12,000 volts. The wire is so long that high
| impedance creates that high voltage.
Why would I assume that?
| Now install a 'whole house' protector that can earth at least 50,000
| amps. How much voltage must the breaker box be to make a trivial 100
| amp surge approach the appliance? 12,000 volts. A 'whole house'
| protector that has limited voltage to 1000 volts clearly will send
| very little surge current to appliances. If that current does arrive
| with no voltage losses (impossible, but if), then 1000 volts
| protection in all computers would make that surge irrelevant. IOW
| protection inside all appliances is not overwhelmed when earthing one
| 'whole house' protector.
And the surge "chooses" to entirely go over one metallic path and just
disregard the existance of another metallic path when it reaches the
junction that lets it go either way?
Your assumption that "whole house" protection is complete protection
is just utterly false.
| And then another concept - equipotential - means even less surge
| energy enters the house. Why would a surge seek earth ground inside
| the house when voltage beneath the house is already near same levels?
| Just another reason why 'whole house' protector is so effective.
Surges do not "seek" anything, except maybe to get away from where they
have been (e.g. forward propogation).
| Why does the telco suffer no damage. Interconnecting everything can
It is not true that they suffer no damage. Damage does in fact occur.
What is true is that the equipment they use is better able to handle
the surges that remain after their diverse entrance protections. But
that is not 100% protection.
| create ground loops - surge damage. That same point was made in
They have no choice but to interconnect things. It's what they do.
So they have to design the protection around that constraint.
| Montandon and Rubinstein's 1998 IEEE paper. (Why do I know so many
| professional sources and papers? Maybe I learned this stuff decades
| ago?) Telcos eliminate surge damage by interconnecting to a single
Or maybe you didn't and just made a lot of incorrect assumptions.
| point earth ground - not interconnecting everything to everything
| else. Their first conclusion (how curious that I have their paper):
The telco equipment is widely interconnected. These days, more and more
of it is interconnected _optically_ and so their exposures are less.
But substantial amounts _are_ interconnected metallically.
|> 1) Whenever possible, a single entry point should be
|> used for all incoming services in order to avoid that
|> part of the lightning current flow ...
|> 2) large loops should be avoided by suitable cable
|> routing inside the building (see figure 10) ...
|> 3) Do not establish equipotenialization by multiple bonding
|> ... to different potential points within the structure.
| which means everything is not interconnected to everything else.
| Telcos use 'whole house' protectors AND bond everything back to single
| point ground. If plug-in protectors work inside homes, then plug-in
| protectors work in telco COs. Telcos don't use plug-in protectors for
| numerous reasons. Ie. plug-in protectors do not even claim to provide
| effective protection. No specs claim that protection.
The "single point ground" is often (and probably usually) a ground ring
or similar kind of grounding system.
Get this through your thick skull:
Plug-in protectors work when the plug-in protector can be applied to
the WHOLE group of interconnected equipment. In a home where the
number of pieces of such equipment typically is half a dozen or fewer
then it it practical to use a plug-in protector. In a telco CO the
plug-in protector would have to have HUNDREDS or THOUSANDS of pieces
of equipment plugged into it. That is NOT practical for an 8-outlet
power strip with a 15 amp plug.
Telcos protect their equipment on a LARGER SCALE where the whole CO
is all protected together in a different way than a home is protected.
It is possible, but not economically practical, for a home to be
protected the way a telco CO is protected.
It is not economically practical, and probably not even possible, for
telco CO to be protected the way a home is protected.
You seem to be totally blind to the fundamental differences.
You seem to be making assumptions that what works in one place will
work just the same in an entirely different scenario.
You have NO CONCEPT of what actually takes place in a surge and thus
you cannot visualize a surge taking place and how it behaves.
| Repeated stated, a protector is only as good as its earth ground.
Repeating does not make it true. The surge isn't listening to you.
| If we don't waste money on plug-in protectors and instead upgrade the
| earthing, then that 1000 volts can be reduced to 500 volts. Another
| example of why a protector is only as effective as its earth ground
| AND why every high reliability facility upgrades earthing.
The portion of the surge that travels over the junction path that ends
up at ground will, when it reaches that ground, be mostly dissipated
into the ground. But this says nothing about the portion of the surge
that went the other way.
But you assume the surge is seeking ground AND knows in advance which
path is the way to ground AND goes 100% to that path.
| What do Florida residents do for no surge damage? Upgrade earthing
| even better:
| http://members.aol.com/gfretwell/ufer.jpg
| http://www.psihq.com/iread/ufergrnd.htm
| http://scott-inc.com/html/ufer.htm
| But again, nothing new or revolutionary. For 100 years, earthing is
| how surge damage was routinely avoided.
The fact is, a great many, and probably the vast majority, of homes have
poor ground now. So upgrading the ground will always help. But it will
not bring the level of protection up to 100%. And it will NOT create a
situation where either entrance protection or point of use protection
fails to provide additional protection.
A building with poor ground will get inconsistent results from whatever
combination of other forms of protection it uses. But this is a building
that is INCORRECTLY WIRED.
| Above is only secondary protection. Better protection means layered
| protection. Each layer is defined only by what defines that layer -
| the single point earth ground. Homeowners should also inspect the
| other layer; their primary surge protection system:
| http://www.tvtower.com/fpl.html
|
| Station personnel created even more surge damage by disconnected
| earthing. Eventually, they needed a professional who eliminated surge
| damage to expensive Nebraska station electronics. How did he
| eliminate surge damage? He fixed and upgraded what provides surge
| protection - earthing. Yes, he even upgraded the (utility installed)
| primary surge protection system. No plug-in protectors were used to
| eliminate all surge damage:
| http://www.copper.org/applications/electrical/pq/casestudy/nebraska.html
But YOU (w_tom) still fail to understand why a telco CO or a TV station
would find it impractical to use a plug-in surge protector.
Again, I will explain it to you:
The primary protection offered by a point of use protector is equalizing
the surge over a group of interconnected equipment. In order for this
kind of protection to be effective, ALL pieces of equipment must be plugged
into this protector. You can do that with your home stereo system by
plugging in the amplifier, tuner, CD player, tape deck, and turntable,
into the same protective device. You can do that with your home theater
system by plugging your TV, DVD player, VHS recorder, and cable/satellite
box into the same protective device (and you MUST also connect the cable,
satellite, and/or TV antenna feed through that protector, as well). You
can do that with your home computer by plugging the computer, monitor,
and the wall warts for the modem, router, LAN switch, and external drives,
all into the same protective device.
If you want to do the same for a telco CO or a TV station, then you MUST
plug ALL the equipment into the same protective device. This is clearly
impractical for a group of over 100 pieces of equipment.
Instead, a telco CO or a TV station will upgrade the entrance protection
they use to be of a type that offers a better level of protection than
the typical home-grade "whole house" protector.
For a home, or even some small businesses, it is more economical to break
apart the functions of protection such that point of use protection is
used. This is more economical protection because of the smaller equipment
groups involved in a home that allows a point of use protective device to
reduce the kinds of surges it is designed to act on.
| How did Orange County FL 911 system eventually eliminate surge
| damage? Again, fixed or upgraded what provides surge protection -
| earthing:
| http://www.psihq.com/AllCopper.htm
Try plugging all their equipment into a single plug-in surge protector.
You can't because they have too much equipment for that to be practical.
So they MUST upgrade their building-scale protection to make it do the
combined job. THEY spent MORE money on this protection than a home
needs to spend to get the same level of protection.
| Why do I know this stuff? We traced surges. We replaced components
| to make surge damaged equipment working. We discovered how plug-in
| protectors even made surge damage easier. Equipment had to suffer
| direct lightning strikes without damage. Solutions learned from
| experience were always less expensive and simple. Protection is about
| earthing which is why the 'whole house' protector is so effective and
| why the plug-in protector does not even claim to provide effective
| protection.
Plug-in protectors commonly do make surges worse when the building and
equipment is wired wrong. Do your surge tracing on a building that is
correctly wired and come back to me with your (negative) results.
| I never said anything was 100% effective. Put numbers to the
| protection (why does he have all these facts and numbers?). From IEEE
| Green Book (IEEE Standard 142) entitled 'Static and Lightning
| Protection Grounding':
Protection is a tradeoff in costs. For a home, having $100,000 in protection
for $10,000 of equipment is pointless. If you're going to pay that much,
just buy 2 extra sets of equipment and hire people to re-install for you when
things get damaged.
For a telco CO or a TV station, $1,000,000 in protection equipment to protect
$20,000,000 in equipment AND millions of dollars of lost revenue in downtime
is money well spent. This is NOT going to involve a power company installed
surge protector in the meter base. Instead, it will be correctly engineering
building grounds, correctly engineered wiring of the building for power and
all metallic communications, industry grade equipment that integrates surge
equalization across connected components in cases where it is economically an
advantage to do so, and the highest quality entrance surge protective devices
that could easily cost more than your whole house.
A telco CO or a TV station has a completely different economic model and a
completely different equipment strategy involved. While there are ways to
make analogies between a TV station and a typical home, these are more complex.
You clearly don't understand the distinction since your analogies assume them
to merely be the same.
|> Lightning cannot be prevented; it can only be intercepted or
|> diverted to a path which will, if well designed and constructed,
|> not result in damage. Even this means is not positive,
|> providing only 99.5-99.9% protection. ...
|> Still, a 99.5% protection level will reduce the incidence of direct
|> strokes from one stroke per 30 years ... to one stroke per
|> 6000 years ...
|
| Properly earth one 'whole house' protector for about $1 per
| appliance. If 99.5% is insufficient, then spend $3000 for plug-in
| protectors. Of course, plug-in protectors do not even claim to
| provide protection. But if an additional $3000 makes you happy, then
| even I will sell one to you. With profit margins that obscene, even I
| would sell you a plug-in protector.
The whole house protector will provide adequate (not perfect, but measured in
an economic sense, all you need) for most of the power loads in a house. Most
of them are lights and cheaper devices that can be easily replaced. There is
no need for a plug-in protector everywhere. Where you put the plug-in protector
is at the groups of equipment of higher value, either in terms of replacement
cost, or in terms of the need for continued use. Do use plug-in protectors on
your stereo system, theater system, and computer system. Also use them, with
care taken to follow instructions exactly, on any health care equipment used
by invalid relative residents. Use them on the security alarm (though these
general do integrate most of their own protection). DO NOT BOTHER protecting
other things like water heater, dryer, stove, clothes washer, refrigerator,
etc. The whole house protection by itself is adequate for THOSE appliances
in most cases.
--
|WARNING: Due to extreme spam, googlegroups.com is blocked. Due to ignorance |
| by the abuse department, bellsouth.net is blocked. If you post to |
| Usenet from these places, find another Usenet provider ASAP. |
| Phil Howard KA9WGN (email for humans: first name in lower case at ipal.net) |